Modbus Interface
« on: December 19, 2005, 11:02:08 AM »
Dear Sir,

I used Modbus Tester to take data from our equipement but I could not get some.Modbus tester has shown recommend as below

Read Status : Modbus Exception 02-ILLEGAL DATA ADDRESS

Would you please advise me about the solution.

Regards,
Anurak

Admin

  • Guest
Modbus Interface
« Reply #1 on: December 20, 2005, 10:18:41 AM »
Hi
The Modbus Exception 02-ILLEGAL DATA ADDRESS means that the data address received in the query is not an allowable address for your slave.

Regards
Andrzej

Niconol

  • Guest
Modbus Interface
« Reply #2 on: March 22, 2006, 01:27:42 PM »
Hi,

The start adress is not in the data area where you can apply your function or start adress + length is out of this area. That means that you can\'t read or write in any data area.
Be carefull writing start adress in deciaml (or in hexa if preceded by 0x).


Sorry for my poor english


by

niconol

KurySoft

  • Guest
Modbus Interface
« Reply #3 on: October 26, 2006, 02:49:14 AM »
ť Dear Sir,
ť
ť I used Modbus Tester to take data from our equipement but I could not get
ť some.Modbus tester has shown recommend as below
ť
ť Read Status : Modbus Exception 02-ILLEGAL DATA ADDRESS
ť
ť Would you please advise me about the solution.
ť
ť Regards,
ť Anurak

Hello Anurak!
KurySoft just released a new software solution ModbusConstructor that will help you to take data from any MODBUS device.
Actually, you can easy build comprehensive data model implemented in target device and see data of any type (integer, long, float, binary, hex or discrete) formated.
Look: http://www.kurysoft.com/products.shtml